Electricians revenge
1 members (Scott35), 36 guests, and 15 robots.
Don, I think there's the rub...code says "pipe", not tubing. I don't think regular copper water TUBE would be ant more acceptable than EMT.
e57 Offline
(5) Rod and Pipe Electrodes. Rod and pipe electrodes shall not be less than 2.5 m (8 ft) in length and shall consist of the following materials.
(a) Electrodes of pipe or conduit shall not be smaller than metric designator 21 (trade size 3/4) and, where of iron or steel, shall have the outer surface galvanized or otherwise metal-coated for corrosion protection.
(b) Electrodes of rods of iron or steel shall be at least 15.87 mm (5/8 in.) in diameter. Stainless steel rods less than 16 mm (5/8 in.) in diameter, nonferrous rods, or their equivalent shall be listed and shall not be less than 13 mm (1/2 in.) in diameter.
Electrodes of pipe or conduit, (I have never done one...) that portion of the cod does not say it need to be listed, or have water in it.
But if a steel or nonferrous rod, it does.
