ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 167 guests, and 23 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#222529 03/19/24 04:59 PM
Joined: Aug 2001
Posts: 335
S
Member
We have an older generator that has a frame, tires and a hitch built onto it. We pull it with a vehicle. The neutral is bonded to the frame and it has a ground wire/rod lug on the frame.
The output is through an L5-30R (3 wire twistloc) recep. We want to change to an L14-30R 4 wire twistloc.
Question: X & Y are the phases. Do we put the existing 3rd wire on the N and attach ground to the frame directly? or am I overlooking something here?

Joined: Aug 2001
Posts: 335
S
Member
My error. It has an L6-30, not L5-30

Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
This really gets down to how you plan to hook it up. If it is an SDS (bonding the neutral and switching the neutral in the transfer equipment) then you must leave the bonding in the generator and establish a grounding electrode. If it is not an SDS, typically using a breaker interlock, you are supposed to lift the bond in the generator. In either case, you really should be using a 4 wire feed so your plan is solid.
I don't think a 3 wire plug on a 120/240 generator was ever legal because it wasn't part of 250-60 back in the olden days (pre 96) when Phil Simmonds said the war was over. requiring 4 wires for the exceptions, ranges and dryers.
I suppose it might have used the old loophole for a feeder to a detached building logic.


Greg Fretwell
1 member likes this: tortuga
Joined: Aug 2001
Posts: 335
S
Member
Thanks. Appreciate it.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5