I don't quite understand when/why the neutral needs to get switched when a generator is involved in a residential system. Can you explain please.
i am installing a manual transfer switch but am wondering if i need to switch the neutral as well?
Thanks
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
The electrical system needs the neutral to be grounded at 1 and only 1 point.
If both your normal Service and your generator have grounded neutrals, when they are connected together you will have the neutral of the system grounded at 2 points, which is a no-no.
If your generator neutral is grounded, you need to switch the neutral; if your generator neutral is not grounded, you can allow it to be connected to the normal system's ground via the system's neutral.
Ghost307
|
|
|
|
Joined: Aug 2006
Posts: 356
OP
Member
|
Thanks Ghost, they (the customer) will be installing a portable generator until a permanent one can be purchased.
Are neutrals usually grounded on the portable units? or it varies? and if it is grounded can i disconnect the neutral from the generator frame? Or i am messing up the listing?
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
There is usually a comment in the instructions of how to lift the bond in the generator if you are making this a non-SDS. (not switching the neutral). I think Hondas come floating and most others are bonded from the factory.
Greg Fretwell
|
|
|
|
Joined: Nov 2007
Posts: 764
Member
|
I’ve never switched a neutral on a resi transfer switch, whether automatic or manual. I just make the appropriate change to the ground connection at the generator itself.
|
|
|
|
Joined: Aug 2006
Posts: 356
OP
Member
|
OK. Thanks.
i think now my question turns to SDS. why would would someone choose not to remove the neutral. or any advantage of SDS or non- SDS?
i know the definition of SDS but i dont think i have a 100% grasp as to why you would have one or wouldn't.
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
I can't think of any good reason to create an SDS in 120/240v systems. Usually you apply this when you would be changing from delta to wye or some other significant system change.
Greg Fretwell
|
|
|
|
Joined: Jul 2007
Posts: 1,335
Member
|
Check with your POCO. a few years ago, I saw a commercial for another POCO and they had a shot on a xfer switch and wasn't switched. I contacted them and they said they didn't want the neutral switch
"Live Awesome!" - Kevin Carosa
|
|
|
|
Joined: Aug 2006
Posts: 356
OP
Member
|
OK thank you for the replies.