1 members (Scott35), 161 guests, and 30 robots.
Scott35 Online Happy OP
Transformers & Feeders: 3Ph 4Wire Open Delta
Five Drawings of Transformer Setups (Connection Schemes);
Primary and Secondary Feeders, Plus OCPDs and Panelboards for:
3 Phase 4 Wire Open Delta Transformers
(Two Voltage SDS)
NOTE: Click on Image to view Full-Sized Image
Drawing 3PH4W-OD1: 480V x 120/240V 3 Phase 4 Wire Open Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V; With Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Drawing 3PH4W-OD2: 480V x 120/240V 3 Phase 4 Wire Open Delta - Center Tap Grounded Neutral
Single Panelboard fed by Secondary Feeders, Additional Panelboard "Subfed".
Drawing 3PH4W-OD3: 480V x 120/240V 3 Phase 4 Wire Open Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V;, With Grounded Conductor)
Two Panelboards fed via Tapped Feeder.
Drawing 3PH4W-OD4: 480V x 120/240V 3 Phase 4 Wire Open Delta - Center Tap Grounded Neutral
Two separate Panelboards fed by Secondary Feeders- each set derived from "X" Terminals.
Drawing 3PH4W-OD5: 480V x 120/240V 3 Phase 4 Wire Open Delta - Center Tap Grounded Neutral
Distribution Panel fed by Secondary Feeders.
Description Text for above images:
Text #3: Two Voltage SDS - Primary & Secondary OCPDs
(Click on Image to view Full-Sized Image)