Electricians revenge
1 members (Scott35), 29 guests, and 10 robots.
#100917 01/22/07 10:50 AM
skipper Offline OP
what is the best way to tap the entrance cable at the meter socket ? also my second panel is 50 ft away do i need to have a disconect just after the meter ?
#100918 01/22/07 11:20 AM
Will your POCO even allow the second meter on this one drop or lateral?
Roger
#100919 01/22/07 11:40 AM
skipper Offline OP
the women i talked to at NStar told me that since i had a 200amp service and was only adding a 100 amp panel that i could just tie into the existing meter and add the second meter. I dont know i dont do res. work. before i talked to the inspector i figure i get some info
#100920 01/22/07 12:31 PM
Is this a lateral or overhead service?
Is NStar your POCO?
Roger
#100921 01/22/07 12:39 PM
skipper Offline OP
NSTAR IS MY POCO and it is and over head with a 4/0 service drop to the first meter
#100922 01/22/07 12:53 PM
4/0 wire .... well, we're not talking about wire nuts here!
In similar situations, I instal a gutter in the service drop, before the meters. There, I make my splices, using NSI / Polaris set screw connectors. The PoCo has no problem with adding a seal to the gutter.
[This message has been edited by renosteinke (edited 01-22-2007).]
#100923 01/22/07 01:53 PM
skipper Offline OP
boy that helps thanks!
#100924 01/22/07 03:08 PM
Now, for the rest of your question, both panels will need disconnecting means grouped together on the exterior of the building. If the existing panel already has a disconnect at the meter you will only need to supply one for the new panel.
Read 230.72
Roger
#100925 01/22/07 10:47 PM
reno, does the poco require you to supply the sealable screwheads?
#100926 01/22/07 11:25 PM
The gutters made by Hoffman come with a small hasp that will accept a seal.
