0 members (), 174 guests, and 29 robots.
#61955 02/06/06 06:44 PM
I don't have a lot of experience with engineering so I am looking for a little help with figuring the lighting demand.
Here are the specs:
119-50watt incadescent lamps
21 -2x4 3lamp lay-ins, 3lamp T-8
23 -flourescent track heads, 2 lamps each
All of the lighting is 120v. The panel is 3phase.
From what I understand, a power factor has to be figured in for the fluorescent portion of the load.
Thanks for any help.
#61956 02/06/06 08:25 PM
e57 Offline
A lot really depends on the use of the space, and what the lighting is. Most of that can be done by VA/sq'. See 220.3(A) through (C), 220.10 through 12 may also be applicable, and there is an example in Annex D-3.
This is a portion of the FPN on 220.10
See 220.4(B) for the maximum load in amperes permitted for lighting units operating at less than 100 percent power factor.
Happy number crunching.... [Linked Image]