176
26
Hello all, thank you for taking the time to read, and possibly offer comment.
First of all, the only noticeable side effect of this issue is that my coaxial lines are not able to hold the prober connectivity for more than a few hours because apparently voltage is building up inside their splitters? The internet connection and the tv on-demand connections do not work due to this. Comcast sent many techs to the house to finally arrive at this conclusion. At which point I called an electrician. He checked the grounding of the house, which at the time was the only thing comcast told me to ask for. $125 later, I could say that everything was properly grounded. The electrician did notice voltage mysteriously coming from my outlets and being emitted from the back of all comcast equipment (not isolated to one piece of equipment, and this is withOUT the comcast inbound line connected. So, I get two more electricians out, and they agree something is going on, but they cannot tell me why, or whether it's a hazard (they do not believe it is). Here is the description from the last electrician who was there:
We found 8 volts present on our multi-meter between the ground outlet and the back of the router box, we found the same 8 volts between neutral and the back of the box. The Router is two prone with no ground. We found the same 8 volt issue with the lamp, also a two prong lamp with a metal base. When we grounded the back of the box to the buildings ground through the water pipe the voltage reading went to 0 – on the router and the lamp. When we put an inline amp probe between the rear of the router and the neutral we found no current. We found the neutral and ground bonded in the panel and to the water system - we recommended adding a ground rod, but we do not believe the lack of a ground rod is causing the issue. We looked for loose neutrals and loose wiring and we did not find any, we did check and tighten your panel connections. We believe the voltage is being induced rather than being a direct short, that’s just a theory.
Anyone got any ideas?
A little more info might lead us to the problem. Were both the router box and the lamp plugged into the outlet when the measurements were made? Did the TV guys try a different router? Was anything hardwired to the router (TV, PC, etc...) during the tests?
This forum is oriented towards professionals.
You are not using trade terms.
Your missive doesn't quite spell out your problem -- other than your system doesn't work correctly.
I'd advise throwing the problem back upon your vendor.
Tesla
Your problem is not electrical, it is within the cable tv system in your home. Get Comcast back out, have them check ALL of the connectors in the house, on the service drop and at the tap. Look for loose fittings, poorly installed connectors, corrosion between the center conductor and shield and damaged cables. Have them replace anything that is not Comcast approved. Make sure all of the connectors are tight-- a little beyond finger tight (except for the fittings on modems, cable boxes and tv's which need to be finger tight only).
Even though the electricians did not find a "loose" neutral I am very suspicious of the integrity of his grounded conductor between the house and the transformer.
thanks for the responses. it's not a comcast issue. We unplugged all comcast lines. Just any piece of equipment (not necessarily a comcast box), and the same 8 volts is read. I assume if this reputable electric company couldn't figure it out, I'm sure my layman's approach to describing the problem here isn't exactly helpful. but thought i would give it a shot. the "issue" was occuring all over the house, not necessarily isolated to one circuit or one piece of equipment.
Posts: 7,382 Likes: 7
Anybody check the earth ground connection at the demark??
I'm the writer of the www.NoShockZone.org blog on electrical safety as well as the moderator of the AC Power & Grounding Forum on ProSoundWeb.com magazine, so I'm very interested in what's going on with your grounding problem. At first blush this appears to be an open neutral feeding your house, but not all the pieces fit. Please email your phone number to mike@noshockzone.org so we can discuss this a bit.
Posts: 9,931 Likes: 34
Is this an analog meter or a digital meter?
Digital? Put a 200k resistor across the leads and try it again (the load of a 20,000 ohm/volt analog meter on the 10v scale) If your voltage goes away, you are chasing a ghost.
At first blush this appears to be an open neutral feeding your house, but not all the pieces fit. An open neutral, usually presents itself as L-N voltages that are not equal. It is quite common to be able to measure a voltage between a neutral and a ground. This has to do with the voltage drop caused by the load on the circuit. I am not sure what problem the OP is trying to mitigate.
"I am not sure what problem the OP is trying to mitigate."
Bingo.
Further, if you can figure a cure, will the OP comprehend what you're telling him?
J M Sokol is his best bet.
At least ECN must come pretty high in the Google standings: he came here.
The OP is also a perfect example of how difficult it can be to translate civilianese to electrician-speak ... and vice versa.
It's that latter point that's the show stopper. The average Joe is going to cross-confuse virtually everything you have to say.
That's dangerous when electro-shock is a possibility.
Civilians will do stuff that would never enter an electrician's head. You tube is filled with such bloopers. It's amazing more amateurs aren't killed.
Tesla
Bingo.
Civilians will do stuff that would never enter an electrician's head. You tube is filled with such bloopers. It's amazing more amateurs aren't killed. Problem I'm trying to mitigate: the coaxial splitters go bad after about an hour of being plugged in. Replace the splitters, then an hour later, internet connection is dropped permanently. comcast sent their line techs to the house to verify that no voltage was entering my house from their lines. The electrician(s) came by and verified that they are seeing 8 volts unaccounted for. As I stated, and as implied by my username, i am no electrician. Just grasping at straws. That's why I provided the summary from the electrician, because I knew I couldn't accurately describe the problem using the appropriate jargon. And yes, I wouldn't likely understand any resolutions that were provided here. However, the "op", while an amateur, isn't an idiot, so I'd never try anything with electricity that I wasn't sure of. There's a difference between civilians and morons. FYI, fios came out yesterday to install their internet, which is a direct line with no splitters. No issues so far, fingers crossed. Lastly, I do appreciate all the responses.
If you are really getting current fed intro the cable I would start with the TVs and other equipment. I had a Daewoo TV that back fed enough into the cable to trip a GFCI. Cable amplifiers are another thing to suspect
The electrician(s) came by and verified that they are seeing 8 volts unaccounted for. The phrase "unaccounted for voltage" is not descriptive enough to be meaningful. for example, do you have 8 volts too much or 8 volts too little? For troubleshooting, the proper voltage measurements to be made are (some places might have 2 hots, like at the service panel): Power Line/Hot to Neutral Line/Hot to Ground Neutral to Ground Cable Shield to Neutral Shield to Ground Center to Neutral Center to Ground Measurements need to be taken at the service entrance,at each receptacle feeding the equipment, and at the affected equipment. It would also be helpful to make these measurements both when the equipment is connected to the cable and when it is not.
The electrician(s) came by and verified that they are seeing 8 volts unaccounted for. The phrase "unaccounted for voltage" is not descriptive enough to be meaningful. for example, do you have 8 volts too much or 8 volts too little? For troubleshooting, the proper voltage measurements to be made are (some places might have 2 hots, like at the service panel): Power Line/Hot to Neutral Line/Hot to Ground Neutral to Ground Cable Shield to Neutral Shield to Ground Center to Neutral Center to Ground Measurements need to be taken at the service entrance,at each receptacle feeding the equipment, and at the affected equipment. It would also be helpful to make these measurements both when the equipment is connected to the cable and when it is not. 8 volts where there should be 0 volts. other appliances were ruled out by flipping each breaker systematically in the house, until all breakers were flipped, and none of them affected the voltage.
8 volts where there should be 0 volts. other appliances were ruled out by flipping each breaker systematically in the house, until all breakers were flipped, and none of them affected the voltage. Still not specific enough. 8 Volts were measured from where to where? Ground prong of receptacle to shield of cable? Neutral of equipment to case of equipment? Ground of receptacle to neutral of receptacle? Case of equipment to kitchen sink? We are not there. The only thing we can do is play 20 questions. Did the 8V ever disappear? Right now I would lean toward there being an issue with the neutral and ground in your neighbor's house. For example, if they lost their neutral connection to the utility, they have a faulty cable box and the cable company ground is poor, it is possible that current, from the neighbor is flowing 'out of their house' on the cable and coming 'into your house' before going back to the utility via your neutral-ground connection.
8 volts where there should be 0 volts. other appliances were ruled out by flipping each breaker systematically in the house, until all breakers were flipped, and none of them affected the voltage. Still not specific enough. 8 Volts were measured from where to where? Ground prong of receptacle to shield of cable? Neutral of equipment to case of equipment? Ground of receptacle to neutral of receptacle? Case of equipment to kitchen sink? We are not there. The only thing we can do is play 20 questions. Did the 8V ever disappear? Right now I would lean toward there being an issue with the neutral and ground in your neighbor's house. For example, if they lost their neutral connection to the utility, they have a faulty cable box and the cable company ground is poor, it is possible that current, from the neighbor is flowing 'out of their house' on the cable and coming 'into your house' before going back to the utility via your neutral-ground connection. All I can do is quote the electrician: We found 8 volts present on our multi-meter between the ground outlet and the back of the router box, we found the same 8 volts between neutral and the back of the box. The Router is two prone with no ground. We found the same 8 volt issue with the lamp, also a two prong lamp with a metal base. When we grounded the back of the box to the buildings ground through the water pipe the voltage reading went to 0 – on the router and the lamp. When we put an inline amp probe between the rear of the router and the neutral we found no current. We found the neutral and ground bonded in the panel and to the water system - we recommended adding a ground rod, but we do not believe the lack of a ground rod is causing the issue. We looked for loose neutrals and loose wiring and we did not find any, we did check and tighten your panel connections. We believe the voltage is being induced rather than being a direct short, that’s just a theory.
Your electrician's troubleshooting skills appear to be limited.
I am guessing, it could take almost 20-30 different voltage measurements just to narrow down your problem. Your electrician gave you three.
I definitely would be looking into the cable system. Are your receptacles wired correctly? Ask your neighbors if they are having problems.
Just for my own thoughts....
The OP says "the coaxial splitters go bad after about an hour of being plugged in."
Sounds like a cable amp?? Isn't a 'splitter' more or less like a terminal block for coax, with nothing to plug in??
I think I would make a tester with a LED and a 1k resistor with an F connector on it. If you have enough current to burn out a balun in a splitter, it will light a LED. Then just start plugging in into boxes until you find the one with the leaky RF can.
Use a bi color 2 wire LED, then you don't care about polarity. One way will be red, the other green and AC will be yellow.
Any Occupancy Sensors or Dimmer switches on this circuit?
First off, agreeing with the difficulty in communication/translation here.
One interpretation I haven't seen yet focuses on the splitters "going bad". I'd suggest a significantly-different potential at Comcast's ground point with reference to the rest of the system, causing current to flow through the devices and coax, damaging the bits inside the "splitter," whatever the OP may be applying that term to.
OP's "electrician" seems to be implying that there's 8V between "everything" and "ground," so I'm going with "OP's ground isn't very well grounded."
Posts: 147 Likes: 3
This sounds similar to what may happen over the coax with bad grounding and fault in another residence. a coax isolator, and local bonding to ground may help. This could probably be found to a better price. http://tinyurl.com/d3bjfy dsk