Didn't mean to confuse anyone.
Section 210.52, before (A), (B) etc. has receptacles that are not considered as being any of the required receptacles covered by 210.52. Those are the ones above 5 1/2 feet; in cupboards; part of a fixture, etc. The switched receptacle in (2) goes to 210.70(A)(1)exception..."in other than kitchens and bathrooms one or more receptacles controlled by a wall switch...instead of lighting outlets." Those should be covered by 406.11. For the reasons that Greg mentions above.
The ones over 5 1/2 feet; in cupboards; etc. should not be covered by 406.11.


Alan--